Forum Discussion
Thanks!
Previously I had created 2 separate datasources for temp and humidity, but I was able to modify yours and added a couple things:
- Description: datasource created to apply to certain models of APC Rack PDUs (AP84XX, AP86XX, AP88XX, AP89XX)
https://www.apc.com/us/en/faqs/FA156179/- Enabled Active Discovery and checks for sensor type temperatureOnly (1) or temperatureHumidity (2) real values from 1.3.6.1.4.1.318.1.1.26.10.2.2.1.5 (rPDU2SensorTempHumidityStatusEntry) before adding instance to devices
Description OID 1.3.6.1.4.1.318.1.1.26.10.2.2.1.3 can be added if the sensor name has been configured on the device, default is "SensorName" so I leave it out and let the instance take the name of the sensor (first and only is 1 in my environment)
R4C9GL
APC suggests that the newer Rack PDUs (rPDU2) monitoring use the 1.3.6.1.4.1.318.1.1.26 values for as described in the link and they do not recommend the old OIDs.
Greate stuff. Thanks
Related Content
- 12 months ago
- 6 years ago